Default OIL Furnaces with Air Conditioning - Most Have Air Flow Problems



Content-Type: text/plain; charset=ISO-8859-1; format=flowed
Content-Transfer-Encoding: 7bit
NNTP-Posting-Host: lncswinas01-pool0-a239.lncswi.tds.net
Message-ID: <[Only registered and activated users can see links. ].net>
X-Trace: newspeer2.tds.net 1152627147 69.128.212.239 (11 Jul 2006 09:12:27 CST)
Lines: 51
Organization: TDS.NET Internet Services [Only registered and activated users can see links. ]
Path: number1.nntp.dca.giganews.com!border1.nntp.dca.gig anews.com!nntp.giganews.com!newsfeed-east.nntpserver.com!nntpserver.com!statler.nntpser ver.com!news.glorb.com!newspeer.tds.net!216.170.15 3.144.MISMATCH!newspeer2.tds.net!not-for-mail
Xref: number1.nntp.dca.giganews.com alt.home.repair:871589

Consumer Warning: OIL Furnaces with Air Conditioning - Most Have Air
Flow Problems
The design of the oil furnace with its ultra large heat exchanger coming
to near the top of the furnace and the blower set to the side of the
furnace represents an engineering airflow problem. The blower set to the
side blows against the heat exchanger and the back of the furnace which
blocks directional airflow velocity thus generating high initial
velocity & static back pressures against the blower.

Most installers set the A-Coil directly on top of the furnace with no
transitions resulting in another restriction and more blocking of
directional velocity air flow and a huge leap in (ESP) static
pressures'. Thermo pride states that the E-Coil must be at least 3"
above the furnace. That might work for a small 1.5 or 2-ton A/C, but
what about required airflow for 3 to 5-ton A/C's?

In my opinion, these low boy oil furnaces should be designed with space
above the heat exchanger depending on the airflow requirements of the
air conditioning application size to be used. There should also be a
transition beginning at the top of the heat exchanger and transitioning
to the intake area of the evaporator coil. This would greatly reduce the
backpressure and improve airflow. The worst place to lose velocity and
generate static back-pressure is below the evaporator coil. Where it
needs the velocity and static pressures' is at the diffusers.

The low airflow probable cause is "an unbalanced airflow heatload
through the evaporator coil, along with "back pressure and extreme
turbulence," due to the evaporator coil being too close to the very
large oil furnace heat exchanger.

With the DX coil set perhaps illegally close to the heat exchanger thus
causing an airflow restriction and wicked turbulence problem, a few of
the coil's circuits may be unevenly heatloaded. Since the liquid
refrigerant is not completely evaporated it will cause the outlet line
that the TXV sensor bulb is on to be too cold and the TEV will shut-down
the refrigerant flow, which can greatly reduce the BTUH capacity of the
DX coil and the entire system. On piston refrigerant control systems, it
may flood back liquid, which could damage the compressor.
My scan of my Thermopride OL 11's - Blower Curve - with a quarter HP
blower motor & only 700-rpm with .5" ESP it won't support 1.5-ton of
cooling airflow!
Study the blower curve graph: .5" ESP equals 400-CFM, that is about
right for only one ton of cooling, not 1.5-ton of cooling! Get what you
paid for!
[Only registered and activated users can see links. ]

- Darrell - udarrell

--
Air Conditioning's Affordable Path to the "Human Comfort Zone Goal"
[Only registered and activated users can see links. ]
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Alt Today
Advertising
Google Adsense
 
This advertising will not be shown
in this way to registered members.
Register your free account today
and become a member on
Home Gardening Forum
Standard Sponsored Links

Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air Conditioning Problem? WORSS Home Repairs Forum 14 11-04-2009 08:54 AM
WARNING - Oil Furnaces & A/C Lack of Airflow Problems! udarrell Home Repairs Forum 0 07-09-2006 06:17 PM
Low water flow, low pressure Steve Home Repairs Forum 3 02-25-2006 02:30 PM
Energy Tax Credit for Efficient Furnaces John R Home Repairs Forum 5 02-13-2006 01:40 AM
~~~~low flow....toilet problems long eddy Home Repairs Forum 5 12-16-2005 08:04 AM


All times are GMT. The time now is 12:31 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Copyright 2006-2008 Home Garden Guides | All Rights Reserved